Slant *        6        Forum
Home Home Home
The Place to Go for Slant Six Info!
Click here to help support the Slant Six Forum!
It is currently Tue Nov 26, 2024 4:38 pm

All times are UTC-08:00




Post new topic  Reply to topic  [ 1 post ] 
Author Message
 Post subject: Fuse link stuff.
PostPosted: Wed Apr 25, 2007 11:39 am 
Offline
Turbo Slant 6
User avatar

Joined: Mon Apr 04, 2005 12:22 pm
Posts: 580
Location: Austin Texas
Car Model:
The following is from an offline discussion between me and slant-6 Dan. He suggested I post here, so here we go:

Quote:
But the question remains: Given the resistivity of a given wire, let us
say for calculation 0.2 ohms per 1000 feet, and given the maximum
acceptable voltage drop in a circuit, let us say 2 percent, how do we
determine the maximum current we can pass through a given length of that
wire before our voltage drop tolerance is exceeded? Or, from the other
direction, given a known current load, how do we determine the minimum
wire gauge needed to avoid excessive voltage drop? And, by extension, how
can we calculate the maximum current capacity of a given wire before the
wire fails?

The fusible link should NOT cause a noticeable voltage drop under normal conditions, and here's why:
OK, the resistivity per foot of the wire you mentioned would be 0.2/1000. The total resistance of your fuse link, R, would be the resistivty per foot times the number of feet. So if you have a 6" link,

R=6/12 * 0.2/1000, or 0.0001 ohms (100 micro-ohms... this should be the first warning that what we're going to calculate may be kinda worthless information!).

For a nominal system voltage of 14 volts (round number), a 2% drop would be 0.28 volts across the link.

Rearranging Ohm's law to solve for current, I=V/R, so I(allowable)=0.28/.0001 or 2800 amps! So in order to produce a noticeable voltage drop the current would have to be astronomical. And by the way, that would mean that the fusible link under those conditions would be absorbing almost 800 watts (Vsquared/R).

This also points out why fuse links are so imprecise- you're multiplying tiny numbers by huge numbers, so ANY variation in the resistance, such as at the connector or if the wire has a broken strand at some point, will make a huge difference in the amount of current that it would take to blow the link.

The other thing neglected so far is that "R" is not constant as the link heats up. You know that it really doesn't take 2800 amps to blow the wire you are talking about, and in fact 100 amps will blow it, right? I mean, you can't run your starter through that wire without melting it, and that draws order-of 100 amps.

So, let's solve for how much power that link absorbs at 100amps:

P=Isquared *R, or 100*100*.0001, =1 watt.


Now waittaminute! 1 watt won't blow a 6" wire either, right? So what's wrong? Why does it, in fact, BLOW when this calculation says it should only absorb 1 watt?!? Well, that 1 watt doesn't blow the wire, but it HEATS it, and R starts increasing dramatically, so in a fraction of a second you have a runaway condition where the resistance is skyrocketing, and the link absorbs enough (hundreds of watts) power to melt copper and thus blow.

That's why its just about impossible to do a simple paper-and-pencil calculation to answer his question, and everyone uses rules-of-thumb (or just fuses!). Yeah, you could put together the simultaneous equations that link reisistivity to temperature, temperature to power absorbed, and power absorbed to current through the link and solve for the room-temperature resistance you should start out with (and that's what SOMEONE did and discovered it always comes out about 4 gauges smaller than the wire to protect)... but SHEESH! If your loads add up to 20 amps, buy a 30 amp breaker and call it a day. And if that one "nuisance trips," buy a 50 amp instead, it'll still be fast enough to protect the feed wiring from going up in flames. That's the real beauty of true fuses and circuit breakers versus fuse links- breakers and fuses respond fast enough and consistently enough that sizing them is not super critical.


Also- ALWAYS size the main wiring on the CALCULATED LOAD! Don't rely on the fuse or breaker to protect the wiring from YOU being an idiot and turning on too many loads at once. The breaker or fuse should only protect from a failure (short circuit) or accidental gross overload (a bad device plugged into a power outlet, for example) not from any load that you could conceivably turn on under normal conditions.

_________________
Image


Top
   
Display posts from previous:  Sort by  
Post new topic  Reply to topic  [ 1 post ] 

All times are UTC-08:00


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Limited